Hi,
Is it possible to display the separator for the Analog Numeric as a decimal point instead of a comma on a T10A HMI?
When I develop and simulate on my development pc it is displayed as a decimal point but when downloaded it is displayed as a comma.
Thanks,
Alan
Analog Numeric Display
-
- Posts: 824
- Joined: Tue Mar 13, 2012 9:53 am
Re: Analog Numeric Display
Try upgrading the unit's firmware and using iX Developer 2.0.463.
Best Regards,
Mark Monroe
Beijer Electronics, Inc. | Applications Engineer
Mark Monroe
Beijer Electronics, Inc. | Applications Engineer
Re: Analog Numeric Display
Hi Mark,
Thanks for the reply, it worked a treat after I updated the HMI firmware.
Regards,
Alan
Thanks for the reply, it worked a treat after I updated the HMI firmware.
Regards,
Alan