When importing af project from E-Designer it imports and converts 30 of 59 pictures, and then fails with the message "Error Importing File" - Failed to import file C:\xxx\xxx\xxx\xxx.mpa
When pressing the OK button, the import is terminated.
The project folder consists of files to the 30 converted pictures, but does not contain a .neoproj file, and then the project cannot be opened.
Is this a known problem?
Is there a fix?
Import project from E-Designer
Re: Import project from E-Designer
Are you using the latest iX Developer 1.31.93?
Best Regards,
Beijer Electronics, Inc.
Ron Lloyd | Applications Engineer
Beijer Electronics, Inc.
Ron Lloyd | Applications Engineer
Re: Import project from E-Designer
Hi Ron.
Yes i'm using the latest iX Developer version 1.31.93.
I've worked a little with the problem, since I added this issue.
The E-Designer project contained blocks with the name "System"
System is apparantly not allowed as a block name, when importing to iX Developer.
I've renamed the blocks to Setup System, which allowed the import project program to go further.
BUT, then I got the next problem
Import project stopped at the Alarms block, which is a system block.
The problem here, was the symbols/pictures on the buttons.
I deleted the symbols/pictures on all buttons on the Alarms block, and also on the System Monitor block, because that was the next problem
Finally I was able to import the E-Designer project into iX Developer \o/
Hope this issue will help other with similar problems, and that Beijer will improve the Import Project function to prevent problems like this
Yes i'm using the latest iX Developer version 1.31.93.
I've worked a little with the problem, since I added this issue.
The E-Designer project contained blocks with the name "System"
System is apparantly not allowed as a block name, when importing to iX Developer.
I've renamed the blocks to Setup System, which allowed the import project program to go further.
BUT, then I got the next problem
Import project stopped at the Alarms block, which is a system block.
The problem here, was the symbols/pictures on the buttons.
I deleted the symbols/pictures on all buttons on the Alarms block, and also on the System Monitor block, because that was the next problem
Finally I was able to import the E-Designer project into iX Developer \o/
Hope this issue will help other with similar problems, and that Beijer will improve the Import Project function to prevent problems like this
Re: Import project from E-Designer
If you would like to send me a copy of the E-Designer project with the import issues, that would be helpful to forward to the developers to use for reference on updating the import functionality.
Best Regards,
Beijer Electronics, Inc.
Ron Lloyd | Applications Engineer
Beijer Electronics, Inc.
Ron Lloyd | Applications Engineer