Alarm, set tag on acknowledge

Post by etmdl »

Hello all,
Is it possible to set up the alarm server so that when a specific alarm is acknowledged, is sets a specific tag?
Thanks for your help

mark.monroe
Posts: 824
Joined: Tue Mar 13, 2012 9:53 am

Re: Alarm, set tag on acknowledge

Post by mark.monroe »

Yes, just add an action to the alarm that fires when the appropriated event occurs.
Snap 2013-03-14 at 07.54.34.jpg
Snap 2013-03-14 at 07.54.34.jpg (24.26 KiB) Viewed 5683 times
Best Regards,
Mark Monroe

Beijer Electronics, Inc. | Applications Engineer