Have analognumeric input value converted before setting tag

Post by AMitchneck »

I have an analog numeric configured to multiply a tag's value by 100 before displaying its value using the tags expressions functionality. I want users to be able to modify the tags value by entering it as displayed. Is there a way to add a "reverse" expression to be used to divide the input value by 100 before setting the tag?
Adam M.
Controls Engineer
FlexEnergy

stuartm
Posts: 61
Joined: Thu Jun 06, 2013 9:21 am

Re: Have analognumeric input value converted before setting

Post by stuartm »

Use the scaling gain and offset feature located in your tags. See Image.