Modbus TCP Unable to Open Port Error

Discussion of application development using iX Developer, including but not limited to getting started, using the functions tab, properties, objects and installation.
Post Reply
memethemyn
Posts: 51
Joined: Fri Apr 27, 2012 12:33 pm

Modbus TCP Unable to Open Port Error

Post by memethemyn »

Hi..

I recevied this message when I want to communicate with the Modbus TCP PLC.

Where is the problem..

I tried everything but I didnt find the solution..

JohnCZ
Posts: 73
Joined: Wed Jun 27, 2012 1:17 am
Location: CZ
Contact:

Re: Modbus TCP Unable to Open Port Error

Post by JohnCZ »

Hi,

It is possible that you have not opened all ports that are required to communicate through modbus.

Example when you need to communicate Beijer HMI and PLC from Mitsubishi through MODBUS TCP, then you need opened the port in PLC.
L_ModBus_TCP.JPG
L_ModBus_TCP.JPG (20.18 KiB) Viewed 8636 times
Test your HMI with PC simulator. If HMI response through PC simulator then the problem is in the other site.

JohnCZ

memethemyn
Posts: 51
Joined: Fri Apr 27, 2012 12:33 pm

Re: Modbus TCP Unable to Open Port Error

Post by memethemyn »

I solve the problem by installing the newest version of ix developer and runtime..

When I run the project on the developer pc there is no error but when I tried on the runtime PC the error is given. So I update the runtime and developer..

Thanks..

Post Reply