Hi, I'm a newbie on Ix Developer.
I need to connect a TA100 panel with a Socomec Diris A40 multifunction meter via RS485.
All works good but the Socomec Diris table give the value with some fraction (example: 230V is transmitted as 23000 so I have to divide by 100 to view the correct value).
Is there any setting to obtain what I need without using script? On other brand there was the setting on the object for doing that.
Sorry for bad english... I'm Italian!
Thank you,
Andrea
edit: Hello,
in the meantime I was able to do what I needed (the post has put more than a month to be approved!!).
Just use the gain and offset parameters of the tag
How to format (mathematical operations) tag?
-
- Posts: 40
- Joined: Tue Nov 22, 2011 3:54 am
- Location: Gjerlev, Denmark
- Contact:
Re: How to format (mathematical operations) tag?
Hello
It's pretty easy
Change the tag in the panel (NOT CONTROLER) to Float
Set Gain to 0,01
It's pretty easy
Change the tag in the panel (NOT CONTROLER) to Float
Set Gain to 0,01
--
Emil Gundersen
JCJelektro.dk
Emil Gundersen
JCJelektro.dk