Anyone can give me any idea in this situation.
My HMI works as Modbus Master in Modbus Network. It communicates with 10 Slaves (PLCs). But now it can only read/write from/to the Slave that has the same address to default station. I configured default station in controller setting is 1, and my HMI can only read/write from/to with the controller that has address is 1.
Thanks in advance.
Help me about Modbus RTU Communication
-
- Posts: 5
- Joined: Fri Aug 08, 2014 10:04 am
Help me about Modbus RTU Communication
Nguyen Manh Hung – Technical Manager
Vu Phuc Technology Co.,Ltd
No 5D, 5/86 Hoang Quoc Viet, Cau Giay , Ha Noi, Viet Nam
Mobile: +84 918.634.091
Email: hung.nguyen@vptechnology.com.vn
Skype: hung.nguyen_vptech
Website: www.vptechnology.com.vn
Vu Phuc Technology Co.,Ltd
No 5D, 5/86 Hoang Quoc Viet, Cau Giay , Ha Noi, Viet Nam
Mobile: +84 918.634.091
Email: hung.nguyen@vptechnology.com.vn
Skype: hung.nguyen_vptech
Website: www.vptechnology.com.vn
-
- Posts: 40
- Joined: Tue Nov 22, 2011 3:54 am
- Location: Gjerlev, Denmark
- Contact:
Re: Help me about Modbus RTU Communication
use more controller drivers, than station's on one.
--
Emil Gundersen
JCJelektro.dk
Emil Gundersen
JCJelektro.dk
Re: Help me about Modbus RTU Communication
Just to complete this issue.
I had a problem with Modbus RTU using several Modbus Master Drivers. One for each Slave. It gave me communication errors.
Together with the Beijer support we found the solution to add just one Modbus RTU Master driver. To address the slaves, you add the slave station number before the register number in the Controller-column in the Tag-list.
So in the Modbus Master column in the tag list.
To access Register 40001 from slavestation number 2, it would be "2:40001".
To access Register 40001 from slavestation number 3, it would be "3:40001".
I had a problem with Modbus RTU using several Modbus Master Drivers. One for each Slave. It gave me communication errors.
Together with the Beijer support we found the solution to add just one Modbus RTU Master driver. To address the slaves, you add the slave station number before the register number in the Controller-column in the Tag-list.
So in the Modbus Master column in the tag list.
To access Register 40001 from slavestation number 2, it would be "2:40001".
To access Register 40001 from slavestation number 3, it would be "3:40001".