I have an X2 control.
I've developed a HMI GUI. I also have a CodeSys program.
I can download the HMI onto the Bejier X2 control and it works perfectly fine with the CodeSys program.
For development what i would like is to be able to mirror what the HMI displays in IX developer. I'm under the impression that i'm able to do this via Run in IX developer but i'm unable to get it to function. When the screen appears in IX developer, i get the error/warning: No PLC connected. I've connected the LAN port on my computer to both LAN A and B but no success. I've given the HMI an IP address on LAN B as suggested in the documentation.
Am i able to do what i'm attempting to achieve?
And if so, what might i be doing wrong? Or are there any instructions out there to show me?
Is it possible to mirror the HMI screen in IX Developer?
-
- Posts: 2
- Joined: Wed Aug 01, 2018 4:26 am
-
- Posts: 13
- Joined: Tue Sep 04, 2018 1:20 am
Re: Is it possible to mirror the HMI screen in IX Developer?
Hello!
You need to change your pc address to static and be on the same subnet as the PLC.
You need to change your pc address to static and be on the same subnet as the PLC.