Non volatile tags
Posted: Sat Oct 01, 2011 2:55 pm
by bastian_c
Hello everybody,
I have a small problem, i need a tag which is non volatile but also a controler tag.
the manual says you cannot have both at the same time.
is there a simple workaround?
greetings
bastian
Re: Non volatile tags
Posted: Mon Oct 03, 2011 10:05 am
by Ron L.
I believe what you are wanting to do is have a value saved on the panel and sent to the PLC when the panel powers up. You should be able to do what you want with a "Write" only controller tag and a Non-Volatile internal tag. Whenever the non-volatile tag changes, you'd want to copy it's value to the controller. The code would look like this.
Code: Select all
void NonVolatileTag_ValueChange(System.Object sender, Neo.ApplicationFramework.Interfaces.Events.ValueChangedEventArgs e)
{
Globals.Tags.ControllerTag.Value =
Globals.Tags.NonVolatileTag.Value;
}
- tag_copy_scrn.JPG (78.88 KiB) Viewed 11307 times
- non_volatile_write_tags.JPG (57.78 KiB) Viewed 11307 times
Re: Non volatile tags
Posted: Thu Oct 13, 2011 7:10 am
by bastian_c
thanx for your reply.
this is a solution that will work for my case.
i didnt try it out at the moment because we used another solution with non volatile tags in the plc which is enough at the moment for this case.
greetings