How does a controller link to a poll group?
I have three PLCs connected to HMI as controllers named PLC1 PLC2 and PLC3
I set up 3 poll groups also named PLC1 PLC2 and PLC3
Each poll group has a different poll rate.
I setup my tags to be assigned to a poll group, eg
Status_1 has addr 00100 (in PLC1 column) and is assigned to poll group PLC1
Status_2 has addr 00100 (in PLC2 column) and is assigned to poll group PLC2
Status_3 has addr 00100 (in PLC3 column) and is assigned to poll group PLC3
Is this correct
How is a controller "linked" to a poll group?
-
- Posts: 824
- Joined: Tue Mar 13, 2012 9:53 am
Re: How is a controller "linked" to a poll group?
Yes, that is correct. The poll group is assigned to a tag and you associate a controller address with that tag.
Best Regards,
Mark Monroe
Beijer Electronics, Inc. | Applications Engineer
Mark Monroe
Beijer Electronics, Inc. | Applications Engineer