ThatGuy
Posts: 10
Joined: Wed Sep 13, 2017 10:20 pm

Allen Bradley program tags

Post by ThatGuy »

Hi all.

I am new to iX, i have been given a beijer touch screen program that needs to be heavily modified to suit a new installation. I have set up communications to between the plc (1756 - L62 Allen Bradley) and I can access the controller tags, what I need to do is access the program tags. I have tried as much as I can think of and have googled it but haven't found anything of use.

Has any body had any experience with this?

Cheers

Gabriel B.
Posts: 13
Joined: Mon Nov 06, 2017 11:19 am

Re: Allen Bradley program tags

Post by Gabriel B. »

You are able to access the help section by going to Tags > Controllers> Settings > Help in the project.

Local Program Tags

To access local program tags use the syntax:

Scope:tag name

Example: Prog1:pump10

Note: Local program tags can not be accessed when using Micro 800 controllers.

Give this a try and see if you get what you are looking for.