Hello;
I have a plc ALLEN BRADLEY and HMI BEIJER IX10T, my HMI is currently connected with a plc MITSUBISHI but all inputs / outputs of this plc are full.
But I want to add a pressure controller with PLC ALLEN BRADLEY and add two (2) tag in HMI for communication.
Hmi give this error message: controller2: comm err: conn 0
1- Controller Configuration, I added the Allen Bradley Controller (see image: the choice controller)
Select Brand: Allen_Bradley
select protocol: Ethernet/IP
2- Settings (see image : settings)
3-Stations(see image : stations)
take please:
HMI IP ADRESS: 10.10.12.40
stations.PNG
stations.PNG (23.49 KiB) Viewed 11714 times
CONTROLLER IP ADRESS: 10.1012.10
any help please
best regards
Attachments
The choice of controller.PNG
The choice of controller.PNG (30.5 KiB) Viewed 11714 times
settings.PNG
settings.PNG (19.4 KiB) Viewed 11714 times

User avatar
Russ C.
Posts: 213
Joined: Thu Nov 16, 2017 3:32 pm
Contact:

Re: controller2: comm err: conn 0

Post by Russ C. »

Hi Abdelhak,

If you're still having issues with this please feel free to email our support group at Support.Americas@beijerelectronics.com

Best,
Russ
Best regards,

Russ
(801) 708-6690
Technical Support
Contact Us

Beijer Electronics AB
http://www.beijerelectronics.us

alexjdickson
Posts: 2
Joined: Tue Mar 08, 2016 6:20 am

Re: controller2: comm err: conn 0

Post by alexjdickson »

Hi
I would change the CPU Rack position to 0(zero)

Regards
Alex

LenDamedy
Posts: 5
Joined: Sun Aug 25, 2019 6:53 am
Location: Canada
Contact:

controller2 comm err conn 0

Post by LenDamedy »

I think, that you are not right. I am assured. I can defend the position. Write to me in PM, we will discuss.