E1022 "transmission error" while uploading from HMI to PC

Discussion of configuring and troubleshooting communication to PLC's or other devices using iX Developer.
Post Reply
apiranthitiss
Posts: 1
Joined: Sat Apr 20, 2019 8:18 am

E1022 "transmission error" while uploading from HMI to PC

Post by apiranthitiss »

Good afternoon.

I am trying to upload the program from an E1022 HMI.
Connection is opening normally, uploading starts also normally but when reaches to "tx drv conf" it stops automatically, "transmission error" is received on e-designer and HMI returns to run mode.

I am using a fabricated Cab30 cable and i have tested three different USB to serial adapters.

Just for your information i am trying to replace the HMI, because functions buttons are not working.

Thanks in advance.

User avatar
Russ C.
Posts: 213
Joined: Thu Nov 16, 2017 3:32 pm
Contact:

Re: E1022 "transmission error" while uploading from HMI to P

Post by Russ C. »

We have noticed with USB adapters the ones that contain the FTDI chip have a higher success rate. Do you know if any of your USB adapters utilize this chip?

Also, what about the buttons are failing?
Best regards,

Russ