Dear Officer.
Thank you for your time for the message.
I am green hand for PLC and HMI Programing.
the following picture show my setting for PLC and HMI
However, My HMI still can not connect to my PLC with COM1(RS232 to RS485).
Please help me where I need change so I can fix it.
Thank you very much
Best Regards
Mei Yixin
How to fix the problem for COMM ERR Station 1 for codesys
-
- Posts: 1
- Joined: Tue Sep 30, 2014 6:49 pm
How to fix the problem for COMM ERR Station 1 for codesys
- Attachments
-
- hmi seting.jpg (46.82 KiB) Viewed 11357 times
-
- plc seting 2.jpg (20.65 KiB) Viewed 11357 times
-
- plc seting.jpg (75.43 KiB) Viewed 11357 times
Re: How to fix the problem for COMM ERR Station 1 for codesy
Hi EndlessSoySouce,
One piece of this puzzle is missing. What is the pin out for your PLC and is a null modem or straight serial cable being used?
Also, the mention of the RS232 to RS485 is odd COM1 on the T7A can only be 232.
Often when we encounter cases such as this it is due to a cabling/configuration issue.
The use of Telegram on the RTS control could also be an issue and forcing a login is not supported i would look into these settings.
One piece of this puzzle is missing. What is the pin out for your PLC and is a null modem or straight serial cable being used?
Also, the mention of the RS232 to RS485 is odd COM1 on the T7A can only be 232.
Often when we encounter cases such as this it is due to a cabling/configuration issue.
The use of Telegram on the RTS control could also be an issue and forcing a login is not supported i would look into these settings.
Best regards,
Christopher