How is a controller "linked" to a poll group?

Discussion of configuring and troubleshooting communication to PLC's or other devices using iX Developer.
Post Reply
Brian
Posts: 13
Joined: Thu Oct 18, 2012 10:24 am

How is a controller "linked" to a poll group?

Post by Brian »

How does a controller link to a poll group?
I have three PLCs connected to HMI as controllers named PLC1 PLC2 and PLC3
I set up 3 poll groups also named PLC1 PLC2 and PLC3
Each poll group has a different poll rate.

I setup my tags to be assigned to a poll group, eg

Status_1 has addr 00100 (in PLC1 column) and is assigned to poll group PLC1
Status_2 has addr 00100 (in PLC2 column) and is assigned to poll group PLC2
Status_3 has addr 00100 (in PLC3 column) and is assigned to poll group PLC3

Is this correct

mark.monroe
Posts: 824
Joined: Tue Mar 13, 2012 9:53 am

Re: How is a controller "linked" to a poll group?

Post by mark.monroe »

Yes, that is correct. The poll group is assigned to a tag and you associate a controller address with that tag.
Best Regards,
Mark Monroe

Beijer Electronics, Inc. | Applications Engineer