Hi,
I have many applications to communicate with Siemens PLCs without problems. In this moment, i'm trying to communicate with the new PLC S7-1500 but without success...
Someone has managed to put the IX communicating with S7-1500?
Communication problems between IX and Siemens S7-1500
Re: Communication problems between IX and Siemens S7-1500
Hi,
S7-1500 is successor of S7-300. Theoretically, it is the same as the S7-300. Look at Instruction connection.
BR
JohnCZ
S7-1500 is successor of S7-300. Theoretically, it is the same as the S7-300. Look at Instruction connection.
BR
JohnCZ
Re: Communication problems between IX and Siemens S7-1500
HELLO,
I also met the problem it is already necessary to put in ix Developer the slot to 1 in the parameters of communication.
Then in TIA Portal it is necessary to go to the cpu and to the properties / protection and checked the box all below to authorize the exchanges towards a HMI.
All to work for me with T12B and one s7 1516.
I also met the problem it is already necessary to put in ix Developer the slot to 1 in the parameters of communication.
Then in TIA Portal it is necessary to go to the cpu and to the properties / protection and checked the box all below to authorize the exchanges towards a HMI.
All to work for me with T12B and one s7 1516.
Re: Communication problems between IX and Siemens S7-1500
Hello, ¿any update about this issue?
I'm interested in purchasing an EXTER T70, to communicate with a Siemens S7 1500.
Thanks.
I'm interested in purchasing an EXTER T70, to communicate with a Siemens S7 1500.
Thanks.
-
- Posts: 3
- Joined: Thu May 08, 2014 3:56 am
Re: Communication problems between IX and Siemens S7-1500
Hello,CIAM wrote:HELLO,
I also met the problem it is already necessary to put in ix Developer the slot to 1 in the parameters of communication.
Then in TIA Portal it is necessary to go to the cpu and to the properties / protection and checked the box all below to authorize the exchanges towards a HMI.
All to work for me with T12B and one s7 1516.
Having similar problem with iXT7A and 1215.
It look that all communications are set correctly.
Of course IP address is different.
HMI communicates with PLC but returns with error 123