Micro830 communication with Beijer HMI T7F
Posted: Tue Aug 05, 2014 8:05 am
by s_vb
Hello Everyone,
I am new at development on Beijer HMI. So don't know much about it.
I am working on Micro830 PLC. I am using Beijer's T7F model (HMI).
How do I create tags in HMI for this controller? As there are no addresses in this PLC like (B3, N7, F8 etc..)
Please guide me.
Thanks,
Shailesh
Re: Micro830 communication with Beijer HMI T7F
Posted: Tue Aug 19, 2014 12:57 am
by Shailesh Bangale
Hello Everyone,
It is not possible to do direct communication with Micro830. We have to use Modbus protocol for same. I hv tried it and worked for me.
Thanks.
Why does it take so much time to get approval for queries from Moderator? As compared to Siemens forum, response to threads is very slow for Beijer iX talk forum. As early the topics get approved, more users will be able to see the posts and can solve it. Thats just little suggestion from me. Because, I have used Siemens forum very oftenly, and I generally get reply within 2 to 3 hours.
Re: Micro830 communication with Beijer HMI T7F
Posted: Mon Oct 21, 2019 10:38 am
by Chris T.
While the modbus driver is a good substitute if you require serial, the ideal driver would be the Ethernet/IP driver under Allen Bradley. There are a few limitations that should be noted in the help file, found by going to Tags-Controllers-Settings-Help in iX, i.e. tags must be globally scoped to be read, no multidimensional arrays, etc.