iX T12B to Mitsubishi FX5U Ethernet - Comm err [Solved]

Posted: Mon Aug 31, 2015 10:20 am
by Transistor
Software
  • iX Developer 2.10
  • GX Works3
Hardware
  • HMI - Beijer iX T12B
  • PLC - Mitsubishi FX5U
Error
HMI shows "Controller 1: Comm err station 0".

Has anyone succeeded in getting these two to talk? IP addresses are OK.

iX Developer is configured as shown below:
Image Image

Note the [port setting above. I can't find any documentation on what the PLC is expecting or what's special about 1025.

The PLC is setup as below with GX Works3:
Image

Anyone got any ideas how to get the two talking? Many thanks.

Re: iX T12B to Mitsubishi FX5U Ethernet - Comm err [Solved]

Posted: Tue Sep 01, 2015 11:47 am
by Transistor
I figured it out.

PLC configuration using GX Works3
Image

Image

HMI configuration using iX Developer


Image

Hit the Controller button ...

Image

Hit the Settings button ...

Image

Image