No reply from PLC
Posted: Wed Mar 30, 2016 6:20 pm
Hello,
I am working on an E-1043 display (Module EM-Profibus DP) connected to a Simatic S7-300 PLC using the X2 port (DP Profibus).
-I have a error msg on the display (No reply from PLC), and the two
LED (ST , OP) of the card (EM-Profibus DP) is ON, (Attached file ).
-When I scanned the PLC network Profibus DP I see the node of the Module
(EM-Profibus DP), Please see the attached picture.
-When I remove the Profibus cable I have a error msg in the display (no
network connection) ,the ST LED is ON , but the OP LED is OFF.
-I used an address type (M ,DB, I, Q) on the display and the PLC for testing the communication, but the communication it does not work.
-The configuration of the PLC is the following .
Type : DP Profibus .
Adress : 1 .
Transmission Rate : 1.5Mbps .
Highest DP Adress: 126 .
-The configuration of the display Panel is the following .
Adress : 2 .
The Controller 1 is the driver S7 Profibus DP.
The Controller is connected in the port EM-Fielbus.
-I selected download Always for driver S7 Profibus DP.
-The Bus Terminator is ON in the first and last units .
-The first unit in the network is the PLC MASTER .
-Is this the only thing to do or the is something else ?
Best regards.
Sebhi Mohammed
I am working on an E-1043 display (Module EM-Profibus DP) connected to a Simatic S7-300 PLC using the X2 port (DP Profibus).
-I have a error msg on the display (No reply from PLC), and the two
LED (ST , OP) of the card (EM-Profibus DP) is ON, (Attached file ).
-When I scanned the PLC network Profibus DP I see the node of the Module
(EM-Profibus DP), Please see the attached picture.
-When I remove the Profibus cable I have a error msg in the display (no
network connection) ,the ST LED is ON , but the OP LED is OFF.
-I used an address type (M ,DB, I, Q) on the display and the PLC for testing the communication, but the communication it does not work.
-The configuration of the PLC is the following .
Type : DP Profibus .
Adress : 1 .
Transmission Rate : 1.5Mbps .
Highest DP Adress: 126 .
-The configuration of the display Panel is the following .
Adress : 2 .
The Controller 1 is the driver S7 Profibus DP.
The Controller is connected in the port EM-Fielbus.
-I selected download Always for driver S7 Profibus DP.
-The Bus Terminator is ON in the first and last units .
-The first unit in the network is the PLC MASTER .
-Is this the only thing to do or the is something else ?
Best regards.
Sebhi Mohammed