Discussion of configuring and troubleshooting communication to PLC's or other devices using iX Developer.
Post Reply
DmitriyS
Posts: 1
Joined: Tue Feb 05, 2019 10:45 pm

Project unloading from HMI panel Beijer iX T4A

Post by DmitriyS »

Hello!
I can not unload the project from the Beijer panel of their T4A. HMI panel with PC pinged. The PC sees the panel and the OctoFACE_T4A_V14 project itself.
But when you press upload, after a few seconds it gives an error "Project upload failed". The HMI panel after this error shows the project transfer window, but in fact the project is not copied anywhere. What's happening?
Attachments
DSC_7078.jpg
DSC_7078.jpg (317.35 KiB) Viewed 5219 times

User avatar
Russ C.
Posts: 213
Joined: Thu Nov 16, 2017 3:32 pm
Contact:

Re: Project unloading from HMI panel Beijer iX T4A

Post by Russ C. »

In iX Developer, before you're able to upload from target, the source code must have been downloaded to the panel.

The steps to take to download the source code are from the Transfer Client to click Advanced -> Download all source code, then click Download
2019-04-08 10_51_32-Transfer Client.png
2019-04-08 10_51_32-Transfer Client.png (23.05 KiB) Viewed 5123 times
Best regards,

Russ