Can settings be changed at runtime? (Slave Station Number, Serial settings,...)
i.e., I don't know what Slave Station Number my customer wants my panel to be. I'd like to control it with a persistent tag, or script.
MODICON Modbus Slave RTU/TCP - settings at runtime?
-
- Posts: 40
- Joined: Sat Jun 02, 2012 7:43 am
-
- Posts: 824
- Joined: Tue Mar 13, 2012 9:53 am
Re: MODICON Modbus Slave RTU/TCP - settings at runtime?
You need to add an action to a button and then press settings when that change active controller dialog box comes up.
Best Regards,
Mark Monroe
Beijer Electronics, Inc. | Applications Engineer
Mark Monroe
Beijer Electronics, Inc. | Applications Engineer
-
- Posts: 40
- Joined: Sat Jun 02, 2012 7:43 am
Re: MODICON Modbus Slave RTU/TCP - settings at runtime?
Ah, that's what that does. Much obliged.