Change active controller through scripting
Posted: Mon Dec 05, 2011 10:34 pm
by rajendra.mahajan
Hi,
I am using iX T10A panel and project developed for two controllers.Tags are assigned to both controllers
My question is how to select active controller through script.
At present we can change the active controller using button with action to change active controller.
Best regards,
Rajendra Mahajan
Re: Change active controller through scripting
Posted: Tue Dec 06, 2011 4:16 pm
by Ron L.
There is currently not a way to do that in script. I will add that to my feature request list.
Re: Change active controller through scripting
Posted: Wed Dec 07, 2011 2:38 am
by rajendra.mahajan
Another possible solution is to use communication driver FX Series ADP/BD 5.07.00 and index the station number for tag(Using index register with internal tag) to communicate with desired controller.
Here the issue is that if the default station defined in communication driver is down HMI will not communicate to the other station set by index register! Why?
Is there any work around to change the default station number through script
Best regards,
Rajendra Mahajan
Re: Change active controller through scripting
Posted: Thu Dec 08, 2011 10:16 am
by Ron L.
There is not a way to change the default station number with script.
The problem you are seeing with the index register has been corrected. I will send you a beta version of the driver.
Re: Change active controller through scripting
Posted: Mon Dec 19, 2011 11:10 pm
by rajendra.mahajan
Dear Ron,
Please send the beta version of the driver
Best regards,
Rajendra Mahajan