Modbus master not sending anything

Discussion of configuring and troubleshooting communication to PLC's or other devices using iX Developer.
Post Reply
charliehbeijer
Posts: 40
Joined: Sat Jun 02, 2012 7:43 am

Modbus master not sending anything

Post by charliehbeijer »

I have a modbus master set up on com1. I have tags mapped to addresses on the modbus master controller. The controller is enabled. The poll group is set to 500 ms.

But it won't send anything out on the com port.

I know I have the com port hooked up OK, because I have another program which sends to com1, and I see my hardware monitor blinking, and I can see the serial data in hyperterminal. But in this program there is no activity on the serial port.
Attachments
mm2.png
mm2.png (80.76 KiB) Viewed 13927 times
mm1.png
mm1.png (34.3 KiB) Viewed 13927 times

mark.monroe
Posts: 824
Joined: Tue Mar 13, 2012 9:53 am

Re: Modbus master not sending anything

Post by mark.monroe »

Try setting some of your tags to Always active. The system will only send out data to the slave if tag values change or if a tag is displayed on a screen that is currently shown on the HMI. With always active turned on, it will continuously poll the tags.

You should also be able to unplug the serial cable from the modbus controller and get a Comm error indicating that the unit can not reach a controller.
Best Regards,
Mark Monroe

Beijer Electronics, Inc. | Applications Engineer

charliehbeijer
Posts: 40
Joined: Sat Jun 02, 2012 7:43 am

Re: Modbus master not sending anything

Post by charliehbeijer »

I changed to Modbus over TCP just to see what would happen. I also set all the tags to "always active" as you suggested. The panel sends out modbus polls at regular intervals, and the slave responds. Good.

But if I change back to serial, what I see in hyperterminal is
"TEST IF ECHO". It sends that out once when the program starts, and then the com port goes silent. There is no polling error popup.

"Hide Comm Error" is set to false.

charliehbeijer
Posts: 40
Joined: Sat Jun 02, 2012 7:43 am

Re: Modbus master not sending anything

Post by charliehbeijer »

I found it.

When it's tcp, the "Default Station" is an index into the station table, default zero. When it's serial, the "Default Station" becomes the node number. Zero is not a valid node number. I changed that to 2, and now it is polling. I see the polls in my slave emulator.

Now I'm getting comm errors on the panel, but that is another issue. At least it's polling now.

mark.monroe
Posts: 824
Joined: Tue Mar 13, 2012 9:53 am

Re: Modbus master not sending anything

Post by mark.monroe »

If your memory addresses are invalid the driver will not send out a command. You have addressing set for Decimal in your controller driver, but your using hex memory addresses assigned to the tags.

Change the Addressing field in your controller driver on the iX panel to hex and it will work.

Holding registers (0x3/0x6*) 400000 - 465535
40000 - 4FFFF Read Hex address range
400000 - 465535 Decimal address range.
Best Regards,
Mark Monroe

Beijer Electronics, Inc. | Applications Engineer