Hi..
I recevied this message when I want to communicate with the Modbus TCP PLC.
Where is the problem..
I tried everything but I didnt find the solution..
Modbus TCP Unable to Open Port Error
Re: Modbus TCP Unable to Open Port Error
Hi,
It is possible that you have not opened all ports that are required to communicate through modbus.
Example when you need to communicate Beijer HMI and PLC from Mitsubishi through MODBUS TCP, then you need opened the port in PLC.
Test your HMI with PC simulator. If HMI response through PC simulator then the problem is in the other site.
JohnCZ
It is possible that you have not opened all ports that are required to communicate through modbus.
Example when you need to communicate Beijer HMI and PLC from Mitsubishi through MODBUS TCP, then you need opened the port in PLC.
Test your HMI with PC simulator. If HMI response through PC simulator then the problem is in the other site.
JohnCZ
-
- Posts: 51
- Joined: Fri Apr 27, 2012 12:33 pm
Re: Modbus TCP Unable to Open Port Error
I solve the problem by installing the newest version of ix developer and runtime..
When I run the project on the developer pc there is no error but when I tried on the runtime PC the error is given. So I update the runtime and developer..
Thanks..
When I run the project on the developer pc there is no error but when I tried on the runtime PC the error is given. So I update the runtime and developer..
Thanks..